I have 3 1KVA Transformers. Acme T 2 53010 S model. I want to transform 240V 3 phase to 480V Three phase. I wired each transformer as 240/480, and then connected them as a delta wye with the 240 side as the delta and the 480 sides as the wye, grounded in the center. I ended up with 1,000 volts on the output. I rewired ea transformer as 240/240, delta wye and ended up with 440V on the output. I can drive a 3 phase 480V motor with it, but I would really like to have 480V.

Any idea what I am doing wrong? Was I wrong to assume I could use 3 480/240 transformers, with the 240v inputs used to get 480V out in a delta wye configuration.

To be specific on the transformer wiring, I connected h2 to h3 on each transformer. X2 to X3. Wired the H1 H4's in a wye. Wired the X1 X4's as a delta. Then put 240V 3 phase on the x side.


JLCPCB – Prototype 10 PCBs for $2 (For Any Color)

China’s Largest PCB Prototype Enterprise, 600,000+ Customers & 10,000+ Online Orders Daily
How to Get PCB Cash Coupon from JLCPCB: https://bit.ly/2GMCH9w

Syed Zain Nasir

I am Syed Zain Nasir, the founder of <a href=https://www.TheEngineeringProjects.com/>The Engineering Projects</a> (TEP). I am a programmer since 2009 before that I just search things, make small projects and now I am sharing my knowledge through this platform.I also work as a freelancer and did many projects related to programming and electrical circuitry. <a href=https://plus.google.com/+SyedZainNasir/>My Google Profile+</a>